75 kva 3 phase transformer
domnic
Electrical Contractor
I have a 75 kva transformer 3 phase delta/Y 480 PRI 208 SEC CAN I FEED IT WITH #3 THHN AND #000 THHN TO MY 208 V PANEL?
What is the calculated load and what size is the transformer secondary conductor overcurrent protective device?
Chris
3 phase 480/208 75kw
Calculated load 50 kw might be a little more in the future. secondary protection 200 amps primary 100 amps
With the additional information you have provided I would say that you would be OK to use #3 copper for the primary conductors and 3/0 copper for the secondary conductors.
Make sure that you comply with one of the rules in 240.21(C) for overcurrent protection of the secondary conductors.
Chris