Hi All,
I am installing a thermoforming machine in my shop which runs on 460V 3phase with a load rating of 40kw. My building has 208V service, so I intend to use a 75KVA 480V - 208Y transformer run in reverse (I know this is not the best thing to do but I will take that risk). According to my limited experience, 40000w/460v = 87 Amps is what I need on the secondary side. In order to know the primary current, if I understand correctly, due to the inrush current, it is based on the capacity of the transformer not the actual draw, ie: 75 KVA/(208*1.732) = 208A. Basically, what I would like to know is what size wire and breaker should I use on the primary 208V side? There will be about 10' between the main panel and the transformer, and about 50' between the transformer and the thermoformer. I suspect 75 KVA might be overkill but my only other option is 45 kVA which would be inadequate.
As a corollary to this question, since 208A 3ph is distributed over 3 wires, why can one not size the wire for 70A each? Why must each wire be capable of carrying the entire current?
thanks
I am installing a thermoforming machine in my shop which runs on 460V 3phase with a load rating of 40kw. My building has 208V service, so I intend to use a 75KVA 480V - 208Y transformer run in reverse (I know this is not the best thing to do but I will take that risk). According to my limited experience, 40000w/460v = 87 Amps is what I need on the secondary side. In order to know the primary current, if I understand correctly, due to the inrush current, it is based on the capacity of the transformer not the actual draw, ie: 75 KVA/(208*1.732) = 208A. Basically, what I would like to know is what size wire and breaker should I use on the primary 208V side? There will be about 10' between the main panel and the transformer, and about 50' between the transformer and the thermoformer. I suspect 75 KVA might be overkill but my only other option is 45 kVA which would be inadequate.
As a corollary to this question, since 208A 3ph is distributed over 3 wires, why can one not size the wire for 70A each? Why must each wire be capable of carrying the entire current?
thanks