tim89s
Member
- Location
- Brush Prairie WA
I have a 480 volt primary delta and a 120/208v wye 75 kva transformer. The secondary load calc came out to be 157 amps. I ran 3/0 to a 200 amp main on the secondary side. The primary side has a 100 amp breaker with #3's ran to the primary side of the transformer. Is this install OK? I am a little worried the #3's are to small but on the other hand I didn't use the full potential of the transformer. Is the 75 KVA a rating, meaning I don't have to use all of the potential that the transformer can put out. Such as, a 225 rated panelboard having 150 amp rated wire feeding it. By the way the 75 KVA transformer was a free so I didn't look into using a smaller transformer. Thanks in advance, Tim