greenspark1
Senior Member
- Location
- New England
I have an existing office space with a 75 kVA 480-208/120V dry type transformer located above the drop ceiling. Per 450.13(B) I don't see this being allowed by the letter of the code. However there is plenty of free space, air movement, the transformer is well supported, and you can access it via ladder after removing ceiling tiles. The HVAC units are all ducted so it's not in a plenum either.
I'm having trouble explaining to the client & electricians what is wrong with this scenario. They are pulling a permit to renovate the space and I expect to run into a Code issue. What is the reasoning to limiting this type of install to 50 kVA? What's so different about this and the exception for all kVA sizes for dry types per 450.13(A)?
I'm having trouble explaining to the client & electricians what is wrong with this scenario. They are pulling a permit to renovate the space and I expect to run into a Code issue. What is the reasoning to limiting this type of install to 50 kVA? What's so different about this and the exception for all kVA sizes for dry types per 450.13(A)?