I have a customer needing a cord to feed his power distribution box. He/they usually rent generators. They don't always get the same size genny but said that a 75kw is the most common one they get. The voltage is 480V 3?. I had already sized the cord he needed to his load which is 160A before I was told about the generator. The cord is 4/0, 4-wire.
He said the generator had a 250A breaker on it.
My question is how the breaker was sized 250A for a 75kw generator?
I looked at a chart for sizing generators that said for a 75kw 480V unit it would be around 112A. Their formula was: kw/(voltage x 1.732)/pf.
So I did the calcs. and it seems to match.
75000/(480 x 1.732)/.80 *assuming pf
75000/831.36/.80 = 112.76A
Where did the 250A breaker come from?
Am I missing something in the calculations?