mdshunk
Senior Member
- Location
- Right here.
About what "size" would you call a service done with one set of 750 MCM aluminium conductors? I'm speculating that it's about 550 amps. :-?
There's a mess of 100 amp panels tapped from a gutter.iwire said:400 amp OCPD with a capacity of 385 amps?
![]()
480sparky said:Conductor size doesn't determine the amperage of the service, it's only a function of it. That starts with the main disconnect/overcurrent size. If your main is 60 amps, you have a 60 amp service. Run 6 parallel sets of 2,000kcmils to it, it's still a 60 amp service.
mdshunk said:There's a mess of 100 amp panels tapped from a gutter.
mdshunk said:There's a mess of 100 amp panels tapped from a gutter.
Presently 5, but they're very messy.480sparky said:How many panels are in a 'mess'?
I'm just scratching my head over the 310.15(C) calculation, and making my 550 amp guess by continuing the logical progression from Table 310.15(B)(6)iwire said:Wow, that is a weird coincidence.![]()
Given that situation IMO your service 'size' is really the 310.16 rating of your service conductors, 385 amps @ 75 C
mdshunk said:I'm just scratching my head over the 310.15(C) calculation, and making my 550 amp guess by continuing the logical progression from Table 310.15(B)(6)
Yes, and probably not. Just trying to get my head around it.iwire said:Can you get an EE to bless this?
Would it be worth it?
It is a pretty nice place. All concrete block walls and concrete span deck floors. I've been to this place doing work many times, and every time is a new adventure. It's a real "treat" to work on. The simplest things are sorely complicated by the unusual construction type and the use of unusual wall and ceiling finish materials.480sparky said:That big a service in a dwelling..... back in the 70's... must have been a helluva house.
I'm going to back to my '70s Codes to see if there's any help there.
mdshunk said:About what "size" would you call a service done with one set of 750 MCM aluminium conductors? I'm speculating that it's about 550 amps. :-?
Yup. One hot tub and possibly a sauna box. That's their wish, anyhow. Matter of fact, the hot tub is sitting there, "ready to be hooked up", as the spa salesman probably told them.chris kennedy said:Sounds like you need add something to this.
Doubt it. It probably was engineered, but back then, no plan review was required in this jurisdiction and the occupants are not the original owners.480sparky said:Could the service be newer than the house?
480sparky said:It lists wire sizes up to 200 amp, so there was no relief in wire sizes back then on any service larger than that. Could the service be newer than the house?