turtlepokerman
Member
- Location
- Omaha
Greetings,
An electrician installed a #10AWG copper wire in my garage for a future electric garage heater. The heater that is sized for the space should be 7500W. When I asked the electrician if the wire would be appropriately sized to power the heater, he mentioned that the wire is appropriately sized and to use a 30A breaker. I came back with the calculations of 7500/240V (Heater Rated Voltage) = 31.25A, so I didn't see how that would work. Then he came back and told me to use a 35A breaker and I would be fine. I'm now concerned that I will not be in compliance with 240.4(D). Can anyone confirm if a 35A Breaker is allowed to protect a #10AWG CU wire being utilized for a garage heater per NEC 2017?
An electrician installed a #10AWG copper wire in my garage for a future electric garage heater. The heater that is sized for the space should be 7500W. When I asked the electrician if the wire would be appropriately sized to power the heater, he mentioned that the wire is appropriately sized and to use a 30A breaker. I came back with the calculations of 7500/240V (Heater Rated Voltage) = 31.25A, so I didn't see how that would work. Then he came back and told me to use a 35A breaker and I would be fine. I'm now concerned that I will not be in compliance with 240.4(D). Can anyone confirm if a 35A Breaker is allowed to protect a #10AWG CU wire being utilized for a garage heater per NEC 2017?