fastline
- midwest usa
- Engineer
In a bit of a debate as this is getting interesting. I have personally inspected this property, which has a 750kva xfmr, serving a building, with a single set of 500mil Al conductors. Not even close to being able to handle the full grunt of that xfmr. Kind of odd if you ask me. Total disconnect ampacity is 460A over 3 disconnects.
Because all this switch gear is getting moved and power has to be cut anyway, I am highly encouraging a repair to get fully ampacity terminated to first OCPDs, which has been agreed. However, there is now the debate of Copper vs Al, sizing, etc. Generally, that short run for me between xfmr and OCPD should never be a compromise, but others are trying to 'factor' it. The reality is that xfmr can handle serious overload, which can be an advantage, and expensive later if you blow up the service wires!
I am recommending 3 sets of 500Al or 2 sets of 750Cu. Obviously you can play with that a bit but I generally size around 75c for rated xfmr so there is headroom for OL. I realized all the tables, factoring, etc. I'd just like to get ideas here.
I have never seen someone take the 4+ conductor hit on a service, but this one only has a single 4" conduit so I am scratching on the best play here. I sort of think someone got shorted here. WTF would you only run a single conduit and conductor set for that size?