Heres the situation...
- 4000A bus
- 3400A main fuse
- (8) sets of 500mcm CU THWN-2
Is the wire sufficiently sized? Or do we need (10) sets?
Here's my thinking...
- with (8) sets, the 75o temp is 3040A, and the 90o temp is 4300A.
- The wire may rise above 75o, but never above 90o. The wire is rated 90o, so the wire itself sufficiently protected.
- The bus is rated 4000A, so it will not be overloaded either.
- The terminals are 75o rated. But is that 75deg at 4000A, or 3040A? Do I consider the terminals part of the bus, or part of the wire? If part of the bus, you can say they will never be overloaded. But if part of the wire, they could rise above 75o and then be overloaded.
FWIW, the design load is 2400A, all continuous (2400A x 1.25 = 3000A).