75KVA transformer primary over current protection

Status
Not open for further replies.

templdl

Senior Member
Location
Wisconsin
And the rest of the story can be found in the NEC art 450. Any wild guesses the the transformer has a common 208y/120 secondary which is all the more reason the read and understand art 450.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
According to Mike Holt's transformer chart a typical 75 kva would use a 125 amp OCPD on the primary and a 225 amp on the secondary.
 

jap

Senior Member
Occupation
Electrician
According to Mike Holt's transformer chart a typical 75 kva would use a 125 amp OCPD on the primary and a 225 amp on the secondary.

I agree.
I got tired of always having to go to the charts for xfmrs.

for 3ph xfmrs for a shortcut I use 1.2 for 480
2.4 for 240
and 2.77 for 208v

In this example primary 75 x1.2 = 90 x 1.25 = 112.50
then secondary 75 x 2.77 = 207.75 x 1.25 = 259.69

JAP>
 