8,000 sq ft art center load calculation

Status
Not open for further replies.

Stevenfyeager

Senior Member
Location
United States, Indiana
Occupation
electrical contractor
An 8,000 sq ft art center has a 200 amp 3 phase service. (208 v) Is this too small ? Its getting remodeled, and with two new heat pumps, 25 kw and 45 kw. It has several art room galleries for artists. It will get all new lighting and total re wire. ( I have only calculated residential loads for many years) I see in the NEC 3 1/2 VA per sq ft lighting and receptacle load 1 VA per sq ft. for office buildings, can I use these ? Any suggestions ? Thank you
 

synchro

Senior Member
Location
Chicago, IL
Occupation
EE
Are there any plans for electric kilns to make pottery?
If so that would need to be included in the load calculation.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Unless I made a math error you have almost 200 amps in heatpump load making one 200 amp service very inadequate.
 