Can I use 8 thhn wire with a 75 degree rating to feed a range receptacle ?
Also, I am involved with a remodel of an existing 8 unit apartment complex and am helping the PE get his load calcs low
as possible...
I am trying to keep the existing underground service feed ( at least using only the existing 3" u.g. conduit) while adding central air conditioning to the existing apts.
Most of the apts are less than 650 sq ft with an existing 100 A load center. To keep the total load calc low, what is the minimum size
range that I can use ? When multiplying by 8 ranges, it adds up..
I will calculate the loads using both the optional and standard method, although I am sure the optional calc SHOULD have a lower total.
The building will have a common dryer/washer, so I won't need a laundry circuit ...
Thanking you for your help & any suggestions...
DHSVCS