D dhsvcs Member Location miami Occupation electrician May 15, 2024 #1 Can #8 alum mc cable be used to feed a residential oven receptacle at 50 amps ? 75 degree rating is 50 amps so it looks like the most reasonable cost, even in a SF residence...
Can #8 alum mc cable be used to feed a residential oven receptacle at 50 amps ? 75 degree rating is 50 amps so it looks like the most reasonable cost, even in a SF residence...
L letgomywago Senior Member Location Washington state and Oregon coast Occupation residential electrician May 15, 2024 #2 Not with aluminum conductors but copper yes. They make SER cable that should be cheaper for a house.
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician May 15, 2024 #3 75°C rating is actually 40 amps. You would need #6 Al for a 50 amp circuit.