Patrick Kennedy
Member
Hi folks,
The question: Should a #8 gauge romex (type NM) wire be protected by a 40Amp DP breaker, or a 50Amp DP breaker.
Here's the situation: A #8 guage Type NM (Romex) wire was ran to the range/oven in the kitchen. This house is only 3-4 years old. There was a 50Amp DP breaker protecting it. While at the home doing some additional work for the customer we changed it to a 40Amp DP breaker as per code requirements.
The electrical contractor that originally wired the house was called by the customer to pay for this mistake in his wiring. Now I am having a challange with our local AHJ on the proper interpretation of the code. It is my understanding the maximum size breaker for all type NM cable (Romex) installations has to be taken out of the 60 degree column of Table 310.16.
I know there are different codes that ultimately point you back to using the 60 degree column. One being; 334.80
The local inspector is saying that they allow a 50Amp breaker on this #8 Type NM (Romex) as per their right under the AHJ rules. They say that there is THHN wire inside the overall jacket of the NM cable. That is why they can allow a 50A breaker. I do not believe that they can do that.
It also is my understanding that there are limitations on what the AHJ can do as per the following:
According to Article 90.4 covers enforcement and Authority Having Jurisdiction may grant special permission. However, these special permissions may not supersede the safety standards of the NEC according to Article 90.2(c) which covers special permission, as well as, Article 90.4. Article 90.4 states "by special permission the authority having jurisdiction may waive specific requirements in the Code or permit alternate methods where it is assured that equivalent objectives can be achieved by establishing and maintaining effective safety".
If someone out there can give me a definite answer on this I would really appreciate it. And if you can state the code articles on it too, that would be very benefical
Thank a lot
Patrick Kennedy
The question: Should a #8 gauge romex (type NM) wire be protected by a 40Amp DP breaker, or a 50Amp DP breaker.
Here's the situation: A #8 guage Type NM (Romex) wire was ran to the range/oven in the kitchen. This house is only 3-4 years old. There was a 50Amp DP breaker protecting it. While at the home doing some additional work for the customer we changed it to a 40Amp DP breaker as per code requirements.
The electrical contractor that originally wired the house was called by the customer to pay for this mistake in his wiring. Now I am having a challange with our local AHJ on the proper interpretation of the code. It is my understanding the maximum size breaker for all type NM cable (Romex) installations has to be taken out of the 60 degree column of Table 310.16.
I know there are different codes that ultimately point you back to using the 60 degree column. One being; 334.80
The local inspector is saying that they allow a 50Amp breaker on this #8 Type NM (Romex) as per their right under the AHJ rules. They say that there is THHN wire inside the overall jacket of the NM cable. That is why they can allow a 50A breaker. I do not believe that they can do that.
It also is my understanding that there are limitations on what the AHJ can do as per the following:
According to Article 90.4 covers enforcement and Authority Having Jurisdiction may grant special permission. However, these special permissions may not supersede the safety standards of the NEC according to Article 90.2(c) which covers special permission, as well as, Article 90.4. Article 90.4 states "by special permission the authority having jurisdiction may waive specific requirements in the Code or permit alternate methods where it is assured that equivalent objectives can be achieved by establishing and maintaining effective safety".
If someone out there can give me a definite answer on this I would really appreciate it. And if you can state the code articles on it too, that would be very benefical
Thank a lot
Patrick Kennedy