B boomtruck New member Dec 3, 2003 #1 What is the max amps for #8 romex off of #6 alum for stove? Had #6 alum and added #8 romex to make long enough. Where in code book does it say it's okay?
What is the max amps for #8 romex off of #6 alum for stove? Had #6 alum and added #8 romex to make long enough. Where in code book does it say it's okay?
electricman2 Senior Member Location North Carolina Occupation Retired Electrical Contractor Dec 3, 2003 #2 Re: #8 ROMEX The ampacity of type NM cable is limited to the 60C value which for #8 copper is 40A.
E eric64 Member Dec 3, 2003 #3 Re: #8 ROMEX Also remember when your splicing dissimilar metals to use an approved method.