No maximum distance between the point of entrance of service
conductors to a readily accessible location for the installation
of a service disconnecting means is specified by
230.71(A). The authority enforcing this Code or AHJ has the
responsibility for, and is charged with, making the decision on
how far inside the building the service-entrance conductors
are allowed to travel to the service disconnecting means. The
length of service-entrance conductors should be kept to a minimum
inside buildings, because power utilities provide limited
overcurrent protection. In the event of a fault, the service
conductors could ignite nearby combustible materials.
Some local jurisdictions have adopted ordinances that
allow service-entrance conductors to run within the building
up to a specified length to terminate at the disconnecting
means. The authority having jurisdiction may permit service
conductors to bypass fuel storage tanks or gas meters and
the like, permitting the service disconnecting means to be
located in a readily accessible location.
However, if the authority judges the distance as being
excessive, the disconnecting means may be required to be
located on the outside of the building or near the building at
a readily accessible location that is not necessarily nearest
the point of entrance of the conductors. See also 230.6 and
Exhibit 230.15 for conductors considered to be outside a
building.See 404.8(A) for mounting-height restrictions for
switches and for circuit breakers used as switches.