If I have a 75 KVA 3ph 480-120/208 transformer. And it is fed with 1/0 AWG wire (150A) for the primary and 250 kcmil (255a) for the secondary with a 150A feeder breaker, can I use the full 75 kva or is it also need a derate to 80% / 60kva?