this if from the '99 NEC, but it is still applicable.
"
As explained in Section 210-20(a) of the 1999 National Electrical Code
(NEC):
?Where a branch circuit supplies continuous loads or any combination of
continuous and noncontinuous loads, the rating of the overcurrent device
shall not be less than the noncontinuous load plus 125 percent of the
continuous load.
?Exception: Where the assembly, including the overcurrent devices
protecting the branch circuit(s), is listed for operation at 100 percent of its
rating, the ampere rating of the overcurrent device shall be permitted to be
not less than the sum of the continuous load plus the noncontinuous load.?
This exception allows for 100%-rated circuit breakers used in equipment
tested and listed for 100% of rating and has led to the phrases ?100%-rated
circuit breaker? and ?standard-rated (80%-rated) circuit breaker.?
Underwriters Laboratories Inc. (UL) specifies tests that must be conducted to obtain listings for continuous operation at 100% of rated current."
Circuit 1
1. Using a standard-rated circuit breaker:
? Minimum required ampacity = (1000 x 1.25) = 1250 amperes
? Because 1250 A is not an available rating, a 1400-ampere circuit
breaker would be required.
2. Using a 100%-rated circuit breaker:
? Minimum required ampacity = 1000 amperes
? A 1000-ampere circuit breaker would be required.
? In this case, the 100%-rated circuit breaker offers two-fold savings:
smaller frame size circuit breakers, which may reduce the size of the end-use equipment and the space needed in the electrical room; and smaller conductors.