lets say you have a 300a 80% rated breaker, so that mean its will be good for 240a. My question is why the label 300a?
QES said:lets say you have a 300a 80% rated breaker, so that mean its will be good for 240a. My question is why the label 300a?
QES said:lets say you have a 300a 80% rated breaker, so that mean its will be good for 240a. My question is why the label 300a?
brian john said:So basically at 240 amps by design it a 300 never trip (assuming no load issues), but in a high ambient with adjacent CB's loaded to 80% of their FLA it may trip.
Fuses and Breakers are rated to continously carry 110% of their rated current at ambient. 25 degrees C for fuses, 40 degrees C for breakers. It's when the OCPD is operating beyond it's ambient that derating should be a consideration.Also be aware that while "open air" fuses themselves are 100%, all fuse holders and switches are only 80% rated just like circuit breakers
davidr43229 said:Fuses and Breakers are rated to continously carry 110% of their rated current at ambient. 25 degrees C for fuses, 40 degrees C for breakers.
thought ambient was not supposed to be an issue until it reached above 40C?
Again, Fuses are designed to run 110% continously at 25 Degrees C. When you increase the ambient, say to 140 degrees F or 60 degrees C the fuse will only carry 90% of it rated current and 70% of it's opening time.You lost me here, standard OCPDs are only rated 80% continuous at less then 40C.
It is vaguely related to the current required to actually cause the device to open the circuit sometime at some temperature. Given the allowed manufacturing tolerance ranges, magnetic versus thermal trip, changes in ambient temperature, phase of the moon, etc, the actual time to trip at exactly 100% of the trip rating could be anything from pretty soon to never; the trip rating is a nominal value, that roughly describes a pretty complex subject.
Exactly ! you "nailed" it.So a 100A breaker will carry 100A continuously asumung adequate cooling, but the NEC requires a load to be calculated at 80% to eliminate nuisance tripping. Is that the case