I have a 800A CB Plug In unit from 4,000A busway for 800A continuous load. 800A CB specified was 100% rated CB so the feeder is sized for (3) sets of 300KCM.
The equipment vendor is proposing we use 1,000A CB with 80% rated, instead. Sounded like they have several 1,000A CB with 80% rated. They are proposing to set the trip at 800A so we don't have to change the feeder size. They said they tested this CB with 800A and didn't exceed the thermal rating.
Cost and physical dimension aside, I have two questions:
1. Code standpoint - Is this code compliant, specifically 215.2 and 215.3.
2. Not clear how 100% rated CB is tested but if 1,000A CB was tested with 800A load and pass the thermal testing, does it make this CB 100% rated at 800A?
The equipment vendor is proposing we use 1,000A CB with 80% rated, instead. Sounded like they have several 1,000A CB with 80% rated. They are proposing to set the trip at 800A so we don't have to change the feeder size. They said they tested this CB with 800A and didn't exceed the thermal rating.