80% rule for branch circuits

Status
Not open for further replies.

bphgravity

Senior Member
Location
Florida
There isn't an 80% rule, but I understand your question. The answer is yes.

a 20A rated breaker is rated for 20A, as long as that load does not operate for more than 3 hours. Therefore, a 16A load run continuously can be protected by a 20A breaker forever.
 

A/A Fuel GTX

Senior Member
Location
WI & AZ
Occupation
Electrician
Just so the OCPD and wire are not too close to the edge. Just a personal choice and not knocking anyone that chooses to take her up to the max.
 

iwire

Moderator
Staff member
Location
Massachusetts
Why though?

Because the breakers we use are not designed to be run at 100% for 3 hours or more.

From the UL General Directory (The White Book) to you


CIRCUIT BREAKERS, MOLDED-CASE AND
CIRCUIT BREAKER ENCLOSURES (DIVQ)


Unless otherwise marked, circuit breakers should not be loaded to exceed 80 percent of their current rating, where in normal operation the load will continue for three hours or more.
 

stickboy1375

Senior Member
Location
Litchfield, CT
Because the breakers we use are not designed to be run at 100% for 3 hours or more.

From the UL General Directory (The White Book) to you


CIRCUIT BREAKERS, MOLDED-CASE AND
CIRCUIT BREAKER ENCLOSURES (DIVQ)

I realize that... but in the residential world continuous loads are far and few.
 

realolman

Senior Member
Although Captain Obvious is not exactly sure what's being discussed here, he feels compelled to be of service.

The load is 80% of the breaker.... the breaker is 125% of the load....

1 /.80 = 1.25.... It's the same thing.:smile:
 
Last edited: