Re: 80% Rule for switchgear
Originally posted by charlie tuna: i have been contracted by engineering groups to monitor service loads over a thirty day period in regards to load expansions, but i don't know if they used the data as "calculated" or to check their "calculations."
I have contracted electrical companies to do the same work. I use the results as follows:
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Take the highest reading during the 30 days.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Convert to KVA (if the readings were in amps)</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Add 25% of the highest reading.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Apply three "correction factors" that account for possible differences in the readings that might arise due to season, due to occupancy level, or due to some "other" factor (that I might apply just to that project). Most of the time, all three correction factors are equal to 1.0. But if the building has a major Air Conditioning load in the summer, and if you take the 30 day readings in the fall, you might have to apply a "seasonal correction factor."</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Add the proposed amount of new load.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">Compare the "total load," as obtained above, to the rating of the equipment. If this does not exceed the rating, I issue the design.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">The State of Washington has a formal process for performing this calculation, and submitting it (along with the plans) for their "permit review."
Originally posted by charlie tuna: . . . and i know monitoring the loads for a month doesn't cover many things.....................
That is why we are required to add 25% to the highest measured load, and why Washington requires us to apply the three correction factors I described above.