80% rule on service breakers

Status
Not open for further replies.

Jnewell

Member
Location
Las vegss
Does the 80% rule apply to service breakers? I am trying to figure out if we can add a pool to this service without an upgrade. We are right under 80% of the load calculation without the pool.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
If you have a proper Article 220 calc that says, for example, 200 amp then you can use a 200 amp main breaker. The "80 % rule" has effect here.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Does the 80% rule apply to service breakers? I am trying to figure out if we can add a pool to this service without an upgrade. We are right under 80% of the load calculation without the pool.
There is no 80% rule for the size of the service. The load calculation tells you the minimum size of the service.
 

Fred B

Senior Member
Location
Upstate, NY
Occupation
Electrician
Other discussion of the 80%rule here:



 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Does the 80% rule apply to service breakers? I am trying to figure out if we can add a pool to this service without an upgrade. We are right under 80% of the load calculation without the pool.
The service ocpd must be sized for 125% of continuous load plus 100% of non-continuous load, unless it is a 100% rated device.
 

JoeStillman

Senior Member
Location
West Chester, PA
I confirmed with NFPA that all of the loads in the resi calc formula are considered non-continuous, so you don't have to multiply by 1.25.

But EV chargers, which don't seem to appear anywhere in 220, are widely regarded to be continuous and not subject to any of the 220.84 diversity factors. I would probably consider a pool filter a continuous load too.
 