I doing an estimate for a small grow house, (yes, we're legal here), and I have a question on the remote cord and plug hid ballasts. The ballasts draw 10.2 amps @ 120v or 5.1a @ 240 v. The boss says i have to use 2008 210.21(b)(2) which limits a 20 amp breaker to 80% or 16 amps plus he wants it reduced again using 210.20 (a), continuous load, to 12.8 amps. This means I can only run 2 ballasts on a 20 amp 240v circuit instead of 3 ballasts. ..
I've done commercial lighting for years and 16 amps was always the number we used for hid's on a 20 amp circuit so i'm a little confused on what the code is actually calling for in this case?
Thanks for any help.
I've done commercial lighting for years and 16 amps was always the number we used for hid's on a 20 amp circuit so i'm a little confused on what the code is actually calling for in this case?