Apologies if this has been done to death before but I am working an issue with the 80% rule as it applies to portable generators...
I have a 60kW diesel gen with a couple of 100amp outputs. My electrical 'go to guy' is saying that according to NEC the breaker for the 100amp connector needs to be 125amp because of the 80% rule if I need 100amps continuous. I feel that a 100amp breaker and a 100amp conductor and a 100amp connector can be expected to run at 80amps continuous. If I need 100amps continuous then I need to upsize everything, the connector and conductor go to 200amp, I can use a 125amp breaker and now the system is sized to run 100amps continuous.
He wants to upsize breaker to 125amps but leave IEC60309 connector at 100amps and not change conductor.
I think this is pushing it, so far as I know IEC connectors are only tested to 110% so you could be pulling 120amps and be 10amps the other side of the connector rating and probably way outside of the existing conductor..
Am I reading it wrong?
Thanks
I have a 60kW diesel gen with a couple of 100amp outputs. My electrical 'go to guy' is saying that according to NEC the breaker for the 100amp connector needs to be 125amp because of the 80% rule if I need 100amps continuous. I feel that a 100amp breaker and a 100amp conductor and a 100amp connector can be expected to run at 80amps continuous. If I need 100amps continuous then I need to upsize everything, the connector and conductor go to 200amp, I can use a 125amp breaker and now the system is sized to run 100amps continuous.
He wants to upsize breaker to 125amps but leave IEC60309 connector at 100amps and not change conductor.
I think this is pushing it, so far as I know IEC connectors are only tested to 110% so you could be pulling 120amps and be 10amps the other side of the connector rating and probably way outside of the existing conductor..
Am I reading it wrong?