I here alot of electricians say you can only place 80%load on the rating of breaker.If the load is non continuous then the load can be at 100% I think.Continuous being 3 hours or more.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: 80%verses100%

Travis,
If the load is non continuous then the load can be at 100% I think
you are correct.

Roger
 

templdl

Senior Member
Location
Wisconsin
Re: 80%verses100%

If the wire is sized properly and the breaker sized to protect the wire this, with almost all certainty, is not an issue.
Look at art 210.19 (A)(1) and 210.20(A)
 

GG

Senior Member
Location
Ft.Worth, T.X.
Re: 80%verses100%

Wouldnt you have to consider 210.23(A)(1) & (2) or are you refering to a load that would not fall in the category of 210.23(A)(1) & (2)? Thanks.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: 80%verses100%

Originally posted by GG:
Wouldnt you have to consider 210.23(A)(1) & (2) or are you refering to a load that would not fall in the category of 210.23(A)(1) & (2)? Thanks.
210.23(A)(1) & (2) is only about the connected loads not the entire circuit.

210.23(A)(1) for example limits one cord and plug connected equipment to 80% of the branch circuit.

So on a 20 amp receptacle circuit you could plug a 16 amp heater in along with a 4 amp TV.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: 80%verses100%

GG, the sections you reference would not change the branch circuit OCPD rules of noncontinuous verses continuous loads.


Roger
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: 80%verses100%

210.23(A)(1) for example limits one cord and plug connected equipment to 80% of the branch circuit.
This would only apply to a multi outlet circuit. A circuit with a single receptacle can be loaded up to 100% of its maximum rating. See 210.23
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Re: 80%verses100%

Originally posted by iwire:
Originally posted by GG:
[qb]

So on a 20 amp receptacle circuit you could plug a 16 amp heater in along with a 4 amp TV.
And just how would a HO know about this rule?

Besides, TVs are continuous loads, seeing as they are on for 3 or more hours continuously. Think super bowl sunday.
 