Given Breaker A, which is an 80A breaker rated at 100% in its application, and breaker B which is a 100A breaker with a standard rating. What is the difference between the two? How do I design a feeder size differently around them in their respective applications?
What you are trying to do is to optimize the cost of your installation.Compare the cost of your cable based upon the 125%_+100% rule. Remember the is all is your load is in fact continuous then the cable is sized to carry 125% of that. The the breaker is sized to protect the cable. Since your cable is sized based upon 125% of the load and the wire has been sized to carry that load the breaker selected is by default is applied at 80% of its rating at a maximum. If you follow this procedure the issue of an "80% rated breaker" is a non issue.
Should you consider optimizing your design by applying a 100% rated breaker then simply us 100% of the continuous load plus 100% of the non continuous load to size your wire. In doing so it is not uncommon for your to be able to a smaller wire to save on cost. BUT, you must use a 90degC rated cable but allied as if it were 75degC. To protect the cable you MUST now use a breaker the is UL listed for 100%. In doing so the 100% breaker MUST be installed per its instructions for it to be used at 100% of its rating.
Keep in mind that you must evaluate the savings but you also can't ignore that 100% rated breakers do cost most.
There even may be s possibly for you to step down a frame size when using a smaller conductor which can save on cost.
If you are designing a distribution system around using 100% rated devices it may make you more competitive.
Another trick is to design your system based upon series rated devices which gives you the opportunity to use devices with a lower kaic rather than more expensive fully rated devices.
If the specs does take exception the using 100% rated and series rated devices then this may allow you to be more competitive than those who design their systems conventionally and use fully rated devices.
Remember that both breakers that are applied at 80% and 100% are identical except for their UL listing. 100% rated breakers will have a solid state trip units. But simply by having a solid state trip unit does not mean that it can be a 100% as it must by UL listed for 100%.