Submitter: Robert W. Jensen, dbi / Rep. BICSI, A Telecommunications
Association
Recommendation: Add new text to read:
800.156 Dwelling Unit Communications Outlets. For new construction, a
minimum of two communications outlet shall be installed; one within the
master bedroom and one within the living room or kitchen, and cabled to the
service provider demarcation point.
Substantiation: Currently there is no requirement for a communications outlet
in a dwelling unit. A communications outlet in the home is needed for many
reasons, but most important is for emergency services such as a simple call for
police, fire or rescue squad.
This proposal only affects newly constructed dwelling units. In addition to
the problem it solves for communications needs in a dwelling, the proposal is
also targeted at safety of technicians and emergency responding personnel
while enhancing the 5 key NFPA strategies to reduce fatal home fires.
1. Reduces the safety risk of electrocution to technicians where extended
length drill bits (54 to 72 inches) are typically used to install cables and
penetrate unseen electrical cables in the attic, wall and ceiling space. (See
pictures at end of this proposal)
2. Reduces the tripping hazard for fire protection personnel during a fire.
3. Reduces the need for home wiring for communications after occupancy
which typically involves tracing, handling, and snaking through electrical cable
pathways and spaces such as in attics and wall cavities which creates
potentially greater hazard (e.g., electrocution).
4. Increases the use of home protection systems and automation which
typically includes fire detection and direct dial-up remote monitoring systems.
5. This proposal ties directly to one of the 5 key NFPA strategies to reduce
fatal home fires (see attached “Fire Loss in the United States During 2002”,
Michael J Karter, Jr., Fire Analysis and Research Division, NFPA).
6. Places communications outlets in homes to address fire safety needs of
young high user communications groups, older adults, and ADA affected.
7. A fine print note is used as a reference to a standard that specifies
installation requirements such as minimum separation from power cabling and
minimum requirements for cabling in support of the FCC mandate for category
3 cable or better. In addition, this standard references several NEC Articles for
meeting minimum requirements.
Note: Supporting material is available for review at NFPA Headquarters.
Panel Meeting Action: Accept in Principle in Part
Add new text to 800.156 to read as follows:
800.156 Dwelling Unit Communications Outlet. For new construction, a
minimum of one communications outlet shall be installed within the dwelling
and cabled to the service provider demarcation point.
Panel Statement: The requirement for at least one outlet within the dwelling
meets the submitter’s intent.
Number Eligible to Vote: 15
Ballot Results: Affirmative: 15