Zamalik7
New member
- Location
- Washington State
I have an existing site where there is a 480V power cable run in the same conduit at communications cables from one building to another. This is considered and undergroudn feeder. The 480V cable has no ground and needs to be replaced. There are no spare conduits to pull a new cable in and all cables run through "Comm" vaults to another building. This is the only path between the two buildings.
1) 800.47A states that conductors shall be in a section separated by means of brick, concrete, or tile partitions "or by means of a suitable barrier". If I replace the 480V cable with an interlocked armored cable is that a "suitable barrier"? Is there any way to pull a new 480V cable in an existing comm. conduit? I do not believe that the comm cables are rated for 600V.
2) Do I need a ground (I have no neutral)?
1) 800.47A states that conductors shall be in a section separated by means of brick, concrete, or tile partitions "or by means of a suitable barrier". If I replace the 480V cable with an interlocked armored cable is that a "suitable barrier"? Is there any way to pull a new 480V cable in an existing comm. conduit? I do not believe that the comm cables are rated for 600V.
2) Do I need a ground (I have no neutral)?