My company has standardized on parallel #600 kcmil for 800 amp feeders.
In the olden days it was normal to use parallel #500.
I was wondering if #500 is still permissable or if there is a specific code that required the change to #600?
Thanks!
Sparky
don_resqcapt19
Illinois
retired electrician
If the 500s are on the load side of an OCPD and if the calculated load is less than 760 amps they are fine. If the conductors are on the secondary of a transformer or if the calculated load exceeds 760 amps, 600s are required.
charlie b
Seattle, WA
Electrical Engineer
And I will add that if nobody has bothered to calculate the load, and if the intent is to use an 800 amp panel with 800 amps of overcurrent protection, then a pair of 500's is not adequate. You have to prove the load is below 760, or you have to assume it is between 760 and 800.
jumper
Well gee Charlie, I thought I kinda said in a way that in post #3.:)
Depends on the calculated load.
Don did also.
charlie b
Seattle, WA
Electrical Engineer
Well gee Charlie, I thought I kinda said in a way that in post #3. Don did also.
No you didn't, Derek, and neither did Don. :happyno: Neither of you addressed the possibility (and, I suspect, a not uncommon circumstance) that nobody actually performed a load calculation. Consider a core and shell installation, with no tenants yet contracted to occupy the space. You put an 800 amp panel into what will eventually be a machinery space or a commercial laundry space or a pinball palace. You can't calculate the load that the eventual tenant will install in that room. So you must presume that the load will exceed 760, and you must use 600's. That was my point.
jumper
Okay, sounds good to me.:thumbsup:
stevebea
Southeastern PA
Don, could you give me the NEC article you are refering to regarding transformer secondary conductors and overcurrent protection. I had a similar situation last week on a 800 amp service. I ordered 600's but someone in the office trumped me and ordered 500's. Thanks!
jumper
240.21(C) Transformer Secondary Conductors. A set of conductors
feeding a single load, or each set of conductors
feeding separate loads, shall be permitted to be connected
to a transformer secondary, without overcurrent protection
at the secondary, as specified in 240.21(C)(1) through
(C)(6). The provisions of 240.4(B) shall not be permitted
for transformer secondary conductors.
stevebea
Southeastern PA
Thank you very much kind sir! :thumbsup:
Thanks again men!!!
This is a service entrance from the load side of the utility company transformer to an office building for future tenants.
There is no way to accurately prove it will calc out to be less than 760 amps so #600's it is.