We are running an 800 amp service from an 800 amp switch in outdoor switchgear to an 800 amp panel inside that has an 800 amp main breaker protecting it.
For sizing the conductors to feed this panel which has provisions for future circuits as well as the known loads to the max the panelboard is rated for are we within
code using (2) 500 MCM THHN conductors which are good for 760 amp total on 75* C scale for terminations. OR do I need to go up to the 600 MCM Rated 840 total?
Reason I asked is the rule that no panelboard should be loaded past 80% of its OCPD protecting it which would be 640 amps.
Their is only 400 amp load connected now but provisions for future.