Hi all -
I'm new to the forum. I have decades of around-the-house&farm experience with wiring, but to date, I've maxed out with 200 amp services.
I'm about to put up a building that will eventually consume about 300kw of singe phase power 220V. The initial phase will be half of that. My local rural utility is helpful and confirmed they can (barely) support the 300kw. They have offered me (2) 167kw transformers, at their cost, including the underground power runs. All of my major internal needs will be 220V based, with an initial load from (80) 1372w computers (e.g. continuous load, no major inrush issues beyond what the power supplies will consume when powered up). That will eventually grow to (200) sources, IF my business model holds up to reality. Since the power supplies require 220v and a C13 plug, I intend to wire (40) 20-amp circuits to single dual NEMA 6-15R recepticas for the initial (80) units, and use C13 -> 6-15P power plugs. Since each socket is rated at 15amps, and I'll be drawing about 6.23 amp, I believe I'll be fine current wise on the receptical, the 20 amp wire, and the resulting 62% loaded 20amp breaker.
The building is split into 2 equal halves, each designed to hold up to (100) sources. I will be wiring one transformer to each side, once I grow enough to justify the 2nd one.
The rest of the path back to the transformers is a bit less definitive. Please correct any statements below that are inaccurate!
I'm thinking of installing (4) Homeline 225amp main lug 30-space panels. Since each 220V breaker will consume (2) spaces, this will allow for the targetted (50) 20 amp 220V circuits with room left for trivial loads like LED lighting. (Math check: 4*30 space, 2 spaces/breaker = 60 potential double breakers... yeah, good.) If I place a max of (13) load circuits in each panel, at 6.23*2 amps each, I'd have a total panel load of 162 amps for a 72% panel breaker load on (2) panels, and a 66% load on the other (2). That works for the individual panels. Total load back on the system would be 623 amps continuous, for a 78% load on a 800 amp main breaker.
Side note: For a long time, I have always used QO panels and breakers, even in static setup situations. Alas, those breakers are almost twice as expensive as Homelites, and I won't be changing the wiring during the life of this project, so I'm having a tough time justifing QO. Please feel free to convince me otherwise.
So: so far we have (80) computers connected to (4) panels, thirsty for juice from one of the 167kw transformers a dozen or two feet away. This is the point where my experience fails me (or if you prefer: I'm exposed to a growth opportunity!). I see that Schneider has an I-line series of panels, some conveniently rated at 800 amps which would mate to the load from my (4) 225 amp panels.
Basically I need to get the power from the meter near the transformer, into a distribution panel, and out to my (4) breaker panels. Without really understanding the I-line series, I presume I can bring the power into one of them, install (4) 225 amp breakers, and just run power to each of the main lug breaker panels? Beyond that I'm lost. NEMA class 1 is fine for this project. Looking at the Schneider and Graybar sites (Graybar to get a feeling for actual vs. msrp pricing) I see I-Line enclosures (the metal box), pricy I-Line interiors (presumably "the guts"), something called a "solid neutral", and last but not least, a seperately priced door (really? People build these without doors???).
Suffice it to say that I always do my best to follow national codes, but the area I live in enforces none (really... not a single government person cared when I built our home beyond the tax collector). As with most projects, money is somewhat tight so looking for ways to save any, usually at the expense of my time and effort.
Any insight and guidance , both in general and specifically around the I-Line portions, would be greatly appreciated. Trying to learn here, please do not simply say "Go hire a licensed electrician". I may end up doing that anyhow, but if I do, I want to be able to intelligently question their proposals.
I'm new to the forum. I have decades of around-the-house&farm experience with wiring, but to date, I've maxed out with 200 amp services.
I'm about to put up a building that will eventually consume about 300kw of singe phase power 220V. The initial phase will be half of that. My local rural utility is helpful and confirmed they can (barely) support the 300kw. They have offered me (2) 167kw transformers, at their cost, including the underground power runs. All of my major internal needs will be 220V based, with an initial load from (80) 1372w computers (e.g. continuous load, no major inrush issues beyond what the power supplies will consume when powered up). That will eventually grow to (200) sources, IF my business model holds up to reality. Since the power supplies require 220v and a C13 plug, I intend to wire (40) 20-amp circuits to single dual NEMA 6-15R recepticas for the initial (80) units, and use C13 -> 6-15P power plugs. Since each socket is rated at 15amps, and I'll be drawing about 6.23 amp, I believe I'll be fine current wise on the receptical, the 20 amp wire, and the resulting 62% loaded 20amp breaker.
The building is split into 2 equal halves, each designed to hold up to (100) sources. I will be wiring one transformer to each side, once I grow enough to justify the 2nd one.
The rest of the path back to the transformers is a bit less definitive. Please correct any statements below that are inaccurate!
I'm thinking of installing (4) Homeline 225amp main lug 30-space panels. Since each 220V breaker will consume (2) spaces, this will allow for the targetted (50) 20 amp 220V circuits with room left for trivial loads like LED lighting. (Math check: 4*30 space, 2 spaces/breaker = 60 potential double breakers... yeah, good.) If I place a max of (13) load circuits in each panel, at 6.23*2 amps each, I'd have a total panel load of 162 amps for a 72% panel breaker load on (2) panels, and a 66% load on the other (2). That works for the individual panels. Total load back on the system would be 623 amps continuous, for a 78% load on a 800 amp main breaker.
Side note: For a long time, I have always used QO panels and breakers, even in static setup situations. Alas, those breakers are almost twice as expensive as Homelites, and I won't be changing the wiring during the life of this project, so I'm having a tough time justifing QO. Please feel free to convince me otherwise.
So: so far we have (80) computers connected to (4) panels, thirsty for juice from one of the 167kw transformers a dozen or two feet away. This is the point where my experience fails me (or if you prefer: I'm exposed to a growth opportunity!). I see that Schneider has an I-line series of panels, some conveniently rated at 800 amps which would mate to the load from my (4) 225 amp panels.
Basically I need to get the power from the meter near the transformer, into a distribution panel, and out to my (4) breaker panels. Without really understanding the I-line series, I presume I can bring the power into one of them, install (4) 225 amp breakers, and just run power to each of the main lug breaker panels? Beyond that I'm lost. NEMA class 1 is fine for this project. Looking at the Schneider and Graybar sites (Graybar to get a feeling for actual vs. msrp pricing) I see I-Line enclosures (the metal box), pricy I-Line interiors (presumably "the guts"), something called a "solid neutral", and last but not least, a seperately priced door (really? People build these without doors???).
Suffice it to say that I always do my best to follow national codes, but the area I live in enforces none (really... not a single government person cared when I built our home beyond the tax collector). As with most projects, money is somewhat tight so looking for ways to save any, usually at the expense of my time and effort.
Any insight and guidance , both in general and specifically around the I-Line portions, would be greatly appreciated. Trying to learn here, please do not simply say "Go hire a licensed electrician". I may end up doing that anyhow, but if I do, I want to be able to intelligently question their proposals.