I have an 800 amp service with a 800 amp 100% rated breaker (75 deg C). Historical peak load is 500 amps. The service latteral is 2 sets of 500 kcmil rated for 760 total amps (380a x 2). I am wondering if this is a code violation. It appears to comply to 230.90 (A) exception #2 which refers to 240.4 (b) which states that you can go up to the next standard size breaker. Next size breaker from 760 is 800. Not sure if the intent is met here though since it may be implied that the breakers are standard breakers and not 100% rated. Anyone run up against this before?