My company i work for has been asked to look at doing some work for a job and I can't seem to make the numbers work at all.
They want to put power to a remote area facility. The distance is 8000 feet from the electrical distribution. At the electrical distribution they have some power quality issues. Not sure what that is. Anyhow, they want to take the existing 460 volt power at the distribution area and put it into a buck/boost transformer. They don't however want to change the voltage. 460 primary, 460 secondary. I have heard that you can use a buck/boost to stabilize the voltage, but this is a little odd for me. On the other end of the 8000 foot run, they want to install a 460 primary, 208/120 secondary transformer. I know I am not the sharpest tool in the shed, but these numbers just dont add up.
8000' run
3 phase power
200 amps
3 runs of 350 MCM
1 run of #2 for nuetral
I guess the the?fella that designed this is a Engineer, but it doesnt work in my calcs.
At 100 amps at 8000' 460, I still get a voltage drop of 10.6%
At 200 amps its like 14.9%
Am I missing something?
Also why would you have the 4 wire and not just a 3 wire in between. Why the neutral, and why would it still be so small?
I have found that the best way to learn about these things is to dig into the calcs and try to figure out why they do what they do. It's just in this case, I can't figure it out!
Thanks
My company i work for has been asked to look at doing some work for a job and I can't seem to make the numbers work at all.
They want to put power to a remote area facility. The distance is 8000 feet from the electrical distribution. At the electrical distribution they have some power quality issues. Not sure what that is. Anyhow, they want to take the existing 460 volt power at the distribution area and put it into a buck/boost transformer. They don't however want to change the voltage. 460 primary, 460 secondary. I have heard that you can use a buck/boost to stabilize the voltage, but this is a little odd for me. On the other end of the 8000 foot run, they want to install a 460 primary, 208/120 secondary transformer. I know I am not the sharpest tool in the shed, but these numbers just dont add up.
8000' run
3 phase power
200 amps
3 runs of 350 MCM
1 run of #2 for nuetral
I guess the the?fella that designed this is a Engineer, but it doesnt work in my calcs.
At 100 amps at 8000' 460, I still get a voltage drop of 10.6%
At 200 amps its like 14.9%
Am I missing something?
Also why would you have the 4 wire and not just a 3 wire in between. Why the neutral, and why would it still be so small?
I have found that the best way to learn about these things is to dig into the calcs and try to figure out why they do what they do. It's just in this case, I can't figure it out!
Thanks