All SqD Equip w/ cu conductors single line setup:
2000A 480 3Ph Main Service --->800A I-Line Sub-Feed CB ---> 800A 480v MGP36800 Sub-Panel Main CB (Trip Unit adjustment set at lowest, #2) ---> 800A lightly loaded I-Line sub-panel ---> 225A I-Line branch Ckt Brkr ---> a (SqD 150T3HF, 180A pri; 416A sec) 150Kva 480x208Y/120v dry type transformer ---> 400A 120/208Y distribution panel Main Breaker.
The transformer was just replaced with a used identical spare from on-site storage with unknown history but told was good. All cabling was checked for opens and shorts as okay. With the transformer's 1st downstream 400A breaker open, energizing the transformer's 225A feed breaker, the 800A sub-panel feed main CB instantly trips. The 225A CB does not trip in the closing process. The 800A main CB's Trip Unit Adjustment hasn't been changed and is set at it's lowest #2 position.
The transformer was changed out due to a failed coil suffered from a nearby lightning strike and had created the same energizing indications we are experiencing now when initially trying to restore power. Does anybody have any helpful experience with this situation they could share? From what I've gathered so far, there might an in-rush current condition with starting up a stale transformer. How is that dealt with if it keeps tripping such a large capacity breaker? Should the trip setting be temporarily adjusted to a longer delay? The instantaneous delay adjustment spans 2-10 times max trip setting. The long time trip is fixed.
Any help or suggestions will be truly appreciated. It's been a lump doing this swap-out so far... A hum is much better than a clunk and silence.