I am sure this has been discussed before, but I cannot find the reference.
I have two existing 3" RGS buried in concrete. I would like to pull eight 4/0 copper THHN-2 and one 1/0 copper ground in each conduit. In the conduit, I can use the 90C rating for 4/0 of 260A but have to derate at 80%. That means I get 416A capacity in each conduit at 90C.
At the terminations, I must use the 75C rating but the conductors are in air, not conduit, so I can use the 75C rating of 360A each. So, each set of parallel 4/0 provides 576A rating, more than the limiting rating in the conduit.
So, since I have two 3" RGS, I can feed the two sets of eight 4/0 copper THHN-2 with an 800A OCPD and meet code. Agree?
The only problem will be finding an 800A OCPD that accepts four 4/0 conductors.
I have two existing 3" RGS buried in concrete. I would like to pull eight 4/0 copper THHN-2 and one 1/0 copper ground in each conduit. In the conduit, I can use the 90C rating for 4/0 of 260A but have to derate at 80%. That means I get 416A capacity in each conduit at 90C.
At the terminations, I must use the 75C rating but the conductors are in air, not conduit, so I can use the 75C rating of 360A each. So, each set of parallel 4/0 provides 576A rating, more than the limiting rating in the conduit.
So, since I have two 3" RGS, I can feed the two sets of eight 4/0 copper THHN-2 with an 800A OCPD and meet code. Agree?
The only problem will be finding an 800A OCPD that accepts four 4/0 conductors.