I have an 800A MCB that trips occasionally and usually takes 10 -15 minutes to reset. The breaker has been replaced twice. Once with a spare and once with a new breaker and still trips trip units turned all the way up. It has gone for six months without tripping and has done it three times in one day. All the equipment fed from the panel has been running when the breaker trips so i dont believe it is caused by a machine starting The Electrical service consists of 5 800A MCB I line panelboards fed from a 1500kva transformer 480/277 secondary. I currently have an analyzer on the panel but have not found the problem any help or suggestions would be appreciated.
Load on panel 380A - 410A with unbalance of 15- 25A
Voltage phase to phase AB 476 AC 477 CB 468
Voltage Phase to Nuetral A 278 B 277 C 270
PF .89