The following is shown on a drawing for a new installation of a transformer and panelbard. It looks like the conductor sizing is appropriate. Am I missing anything?
Most loads will be 3W 480V.
- Panelboard: 480Y/277V 800A bus with a 800A main breaker. NEMA3R rated.
- Transformer: 500KVA Primary 12470V Secondary=480Y/277V Primary OCPD=100A fuse link
- Grounding electrode at transformer: 3/4" dia. Cu clad steel ground rod 10' long GEC:#2/0 AWG Cu
- Secondary conductors: 3 sets of 3C 300KCMIL THHN Cu (Phase) and 1C 2/0 THHN Cu (Neut); each set pulled in a buried 4" rigid PVC conduit 25' long
- Grounding electrode at panelboard: Building steel that is bonded to plant ground grid GEC: #2/0 AWG Cu
Most loads will be 3W 480V.