You can have 2 400 amp disconnects or 4 - 200 amp disco. either way is finewhen feeding an 800A service via parallel al750's, is it necessary to terminate into one 800A service disconnect, or can each set be terminated into separate 400A service disconnects?
parallel feed through the ct's then into a gutter on the inside, dropping each set of the parallel into its respective 400A d/c
parallel feed through the ct's then into a gutter on the inside, dropping each set of the parallel into its respective 400A d/c
310.4 Conductors in Parallel.
(A) General. Aluminum, copper-clad aluminum, or copper conductors of size 1/0 AWG and larger, comprising each phase, polarity, neutral, or grounded circuit conductor shall be permitted to be connected in parallel (electrically joined at both ends).
As Gus stated, you should drop the reference to parallel.
You are only joined at one end.