I found this old thread but didn't really get an answer I'm confident in.
My drawings call for an 800A service with (2) runs of 600MCM. The customer has taken an alternate to install aluminum conductors to save cost. Would the following satisfy the requirements for an 800A service. (2) runs of 750MCM aluminum (385A*2=770A) fused at the next size up =800A.
My concern is that the wire will not be rated for the full 800A. The terminations are rated at 75 degrees. I realize I can swap the terminations for 90 degree and be home scot free, but if I'm able to, I'd like to do it the way described above.
800 Amp Service
I am going to figure Alu. conductors, would you run 2 pipes with #800 xhhw or more pipes / smaller wire. I had in my head #750 would work but looking at ampacities I don't think I can skip over the #800 when using the 800 or less exception. The service is 277/480 3 phase 800 amps.
forums.mikeholt.com
My drawings call for an 800A service with (2) runs of 600MCM. The customer has taken an alternate to install aluminum conductors to save cost. Would the following satisfy the requirements for an 800A service. (2) runs of 750MCM aluminum (385A*2=770A) fused at the next size up =800A.
My concern is that the wire will not be rated for the full 800A. The terminations are rated at 75 degrees. I realize I can swap the terminations for 90 degree and be home scot free, but if I'm able to, I'd like to do it the way described above.