Sparky4074
Member
- Location
- Chaska, Minnesota USA
I was wondering if I can get some input on a install I have going on. A new 800HP 480V 3PH compressor is being installed and doing the calculation (Name plate is 850A X 1.25 for CD = 1062.5. The issue I have run into is the pecker head has 2 - 4'' threaded hubs for conduit entry. Considering I only have 2 entries it would require me to run 2 parallel runs of 1000 kcmil and good luck terminating that in the pecker head. I was looking into DLO/RHH listed cables but that is getting hard to figure as most specs list the ampacities based on free air. The motor leads in the pecker head consist of 4 sets of 2/0 DLO. Any help and expertise would be greatly appreciated.