cbrown
Member
- Location
- Anchorage, Alaska
I was recently managing the install and cutover of network hardware at a remote facility and ran across something that struck me as wrong. I of course got into a -discussion- with the facility power journeyman on site. I am just that darn network eng , but in this case I think the local power crew is in error.
There is a peice of radio comms gear (PtP 802.16 bridge) mounted in a weathertight enclosure on the outside of the building. The enclosure metal, and has a non-conductive feed-thru the the inside (concrete wall).
The radio unit chassis is bonded to the enclosure.
The radio unit power is standard grounded 120v to a recep inside the building on the wall, the recep is a std #12 H-N-G to a dedicated breaker.
There is a #6 run from the enclosure to a 5/8" 10' rod directly below the enclosure.
This seems OK under 250.54 (I think that is the right article) as an additional ground, as rod to enclosure to radio chassis to #12 egc seems to qualify.
The argument was about the mast and coax bonds.
The mast is #10 green insulated bond to the enclosure.
The coax has a bulkhead style protecter, bonding the braid to the enclosure.
By my understanding, the mast and coax bonding runs must terminate on the grounding electrode system, or an extension of such. *NOT* the additional electrode allowed under 250.54
Am I totally off here?
There is a peice of radio comms gear (PtP 802.16 bridge) mounted in a weathertight enclosure on the outside of the building. The enclosure metal, and has a non-conductive feed-thru the the inside (concrete wall).
The radio unit chassis is bonded to the enclosure.
The radio unit power is standard grounded 120v to a recep inside the building on the wall, the recep is a std #12 H-N-G to a dedicated breaker.
There is a #6 run from the enclosure to a 5/8" 10' rod directly below the enclosure.
This seems OK under 250.54 (I think that is the right article) as an additional ground, as rod to enclosure to radio chassis to #12 egc seems to qualify.
The argument was about the mast and coax bonds.
The mast is #10 green insulated bond to the enclosure.
The coax has a bulkhead style protecter, bonding the braid to the enclosure.
By my understanding, the mast and coax bonding runs must terminate on the grounding electrode system, or an extension of such. *NOT* the additional electrode allowed under 250.54
Am I totally off here?