Endrid Cold
New User
- Location
- Louisville
- Occupation
- Electrician/Utility worker
Today I was investigating an electric meter with no display at a pumping station near our flood walls. It’s a 3 wire 480v UNGROUNDED delta bank. I checked voltage in the secondary side of the PT (metering transformer) and read 15 volts. When I checked the primary side of the PT I read 830v. That seemed impossible. I followed the lines feeding the bank back to the pole the primary tap was on. I noticed 2 cut out fuses on the pole were hanging open. So, only one phase was being delivered to the delta bank feeding the pumping station. How is one phase of a 480v system delivering 830v? And, is it a coincidence that the 830v I’m measuring is equal to 480v multiplied by 1.732, the square root of 3?
Tomorrow I’ll get a serviceman to close those 2 cutout fuses for me and see if the voltages normalize. Also a good chance my PT’s are ruined.
Tomorrow I’ll get a serviceman to close those 2 cutout fuses for me and see if the voltages normalize. Also a good chance my PT’s are ruined.