I have L1 L2 L3 and G
running from a 277/480 generator ( it is not grounded) to a disconnect (which has a connection to a ground rod)
The disconnect feeds a panel board( which has no line to neutral loads ) the panel board feeds a 208/ 120transformer
The transformer is grounded to the same ground rod as the disconnect and it
Has the system bonding jumper
So I have l1 l2 l3 n and g in the panel board
The panel board is feeding some 208v light poles and each pole has an auxiliary ground rod
The problem is that if I measure from remote earth to the ground rod I got 85 v
The lights poles flickers and after a while the breaker trips
I found out that in the 208 /120 panel board had the main bonding installed so I removed it and I thought that was the problem but it's still doing the same thing
All this is really close to transmission lines
Thanks for your time
I'll really appreciate your help thanks
running from a 277/480 generator ( it is not grounded) to a disconnect (which has a connection to a ground rod)
The disconnect feeds a panel board( which has no line to neutral loads ) the panel board feeds a 208/ 120transformer
The transformer is grounded to the same ground rod as the disconnect and it
Has the system bonding jumper
So I have l1 l2 l3 n and g in the panel board
The panel board is feeding some 208v light poles and each pole has an auxiliary ground rod
The problem is that if I measure from remote earth to the ground rod I got 85 v
The lights poles flickers and after a while the breaker trips
I found out that in the 208 /120 panel board had the main bonding installed so I removed it and I thought that was the problem but it's still doing the same thing
All this is really close to transmission lines
Thanks for your time
I'll really appreciate your help thanks