Re: 85 KW Emergency Generator Fuel Source?
It may be up to the AHJ. Natural Gas may not be considerable available in a emergency. If the generator is an art 700 or 701 application, then diesel fuel may be the only choice. Diesel is not a flammable liquid (as is gasoline), so diesel is the fuel of choice for standby generators. Propane can be used, but there are limits on the sizes of a propane tank.
However, a generator on natural gas is a very clean burning installation, and requires little maint. A generator on diesel fuel has to be load tested yearly, to burn off the combustion byproducts.
Natural gas is a good choice, but codes and the AHJ-not the electrical AHJ- may require diesel