I have a situation where an AC unit is being upgraded. The existing circuit is 8awg XHHW AL, approximately 85’ located mainly inside a conditioned space between floors & walls, not in attic or crawl space.
I know article 440 allows the minimum circuit amp rating of the equipment to determine the conductor size. The MCA rating of the unit is 37A, but the MOCP is 60A.
The existing breaker size is 30A. Article 310.15 states XHHW is rated for 75°C /40A installed upto 100’ in an 86° temp location. Obviously all lugs must be rated at 75°C or higher.
I’m not so comfortable throwing in a 60A breaker on this circuit. I’m thinking a 40A breaker, and install a hard start kit on the equipment to help reduce inrush current time.
Any thoughts???