9 current carrying conductors
pedro1200
Ny
I have a question. Does the 9 ccc as a magic number for Thhn and emt combo only applies to 1 inch conduit? 9 ccc plus its associated neutral conductor assuming theres no multi wire circuits will bring the total to 18 conductors (not counting the egc)
If all in the same raceway over 24" long derating required. Pipe size would not effect the rule. The current Is on both the line ( ungrounded) and the natural ( grounded) conductors.
If applies to any circular raceway not just 1" EMT. The reason 9 CCC's and THHN is a magic number is because when you use #14 or #12 conductors their typical ampacity of 15 and 20 amps will not be exceeded even when you apply derating.
For Example:
#12 THHN=30 amps@90° C
9 CCC's= 70% ampacity
30*70%=21 amps still good on a 20 amp circuit.
For Example:
Thanks
For Example:
thanks
Neutrals count, so you couldn't have 9 of each neutral and hots as that would be 18 CCC.
You seldom will ever come out with 9 CCC unless you have a 2-pole single phase or 3ph. With single phase, you end up with 8 CCC, 4-hots, 4-neutrals.