This is a study question for the masters test that a friend asked about.
A school has 9 10kw ranges for a cooking class. The ranges are 240v single phase, the feeder is 240v three phase. What is the amperage for the ranges on the feeder.
I went to table 220.55 and looked up 9 ranges in columb C and got 24kw.
Next I divided by 240 volts and got 100 amps. Then I divided by 1.73 and got 57.80 amps.
I ignored 220.86 because I did not see that it applied to the standard method.
The book answer was 88 amps.
What did I do wrong?
A school has 9 10kw ranges for a cooking class. The ranges are 240v single phase, the feeder is 240v three phase. What is the amperage for the ranges on the feeder.
I went to table 220.55 and looked up 9 ranges in columb C and got 24kw.
Next I divided by 240 volts and got 100 amps. Then I divided by 1.73 and got 57.80 amps.
I ignored 220.86 because I did not see that it applied to the standard method.
The book answer was 88 amps.
What did I do wrong?