90 deg. C to size coductor

Status
Not open for further replies.

Toros

Senior Member
Location
Tujunga, CA
Hi
in what circumstances I can use 90 deg colum of 310-16??
Can I use that to size large underground copper conductor feeding a big service (And temparture derate per correction factor)?????

Thank you
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
You can use the 90 degree rating for derating purposes but for the most part the terminals will limit you to the conductors 75 degree rating.
 

JFletcher

Senior Member
Location
Williamsburg, VA
Hi
in what circumstances I can use 90 deg colum of 310-16??
Can I use that to size large underground copper conductor feeding a big service (And temparture derate per correction factor)?????

Thank you

You can use 90*C column if the terminations are 90*C or higher on both ends. An example of this would be Polaris connectors; the wire between them, you can use the 90*C column. For example, breaker panel/breaker (75*C) to j-box underneath with Polaris connectors (90*C), then the main run to another j-box with Polaris connectors (again, 90*C), up to say a disconnect (75*C).

It can make a big difference in wire use if you're right on the edge of wire size/ampacity. For example, using the 90*C table, you can use copper 500MCM for 425A. If you used the 75*C table, you'd need 750MCM or two sets of 4/0 vs 3/0 (or 1000MCM AL vs 750MCM, or two sets of 300MCM vs two sets of 250MCM AL), and probably larger conduit for those wires. From the connector to the breaker/disco, you'd need the copper 750MCM, but if we're talking a 1500+' run of cable, you could potentially save thousands of dollars by using the 90*C column 98% of the way. On top of that, by using two large j-boxes, instead of 90's, you're making your wire pull that much easier.
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
I agree with JFletcher. In my opinion, if the ends are free for-at least- 24"[600 mm] and rated for 75oC you may take 90oC for underground. A open cable tray-see NEC Art.392.80 90oC underground 75oC on open tray.jpg
 