I meant to expand on my question #2
......Where I get a little confused with this is there are TWO tables you must refer to when doing a correction factor. 310.15(B)(1)(1) and then 310.15(B)(16). So, first, I would go to 310.15(B)(16) and use the 90 degree column? Then which temperature column would I use for the multiplier in 310.15(B)(1)(1)?? 75 degree or 90 degree? So if your always using the 90 degree column when doing correction( and adjustment) when would one ever use the 60 or 75 degree columns for correction multiplier?
Some of the listed conductors would not qualify for the 90 c table. This is when you use 60 or 75 to start then move to ambient.
An example would be if you look at the table for THWN.
Is it listed as 75c
In order to use the 90c is has to have -2.
For me the words condition of use is the key.
Using the THWN, let's say it is a THHN / THWN conductor.
This conductor has a 75c and a 90c rating. So which to use?
The KEY, condition of use. Based on the letters and the location the conductor is installed will be you quide to choice.
TH
WN would be a 75 c location
Wet. The THHN rating is for DRY only.
If the conductor was in raceway above grade in a dry location 90c can be used. If the conductor was installed in a wet or combination of wet and dry you would use 75c to start.
If the conductor had -2 than you you could 90c to start for both wet and dry locations.
Another item of importance with the letter designators are continues use. This was mentioned above so don't read past it. You would need to consider the condition of use.
A designation of -2 is contiuous use wet or dry at 90c. For the T
HHN, it is rated for 90c c continuous use Dry location only. The (HH) of the THHN tells you continuous use.
These letters will direct you to the correct column to start with.
Reviewing the table you will see that the 60c has no H letters. So any conductor without this (H) letter has to start at the 60 c table.
Read thru part 2 of 310 installation.
310.10 will help shed light on letter designators. I will also post a pic which hopefully will help future on choosing the correct column.
Then read 310.15 looking close at (3).
See 110.14 and look at (C). While your there I would recommend read all of 110.14.
This should set you on. The right path to make a decision on using the correct column for the conductor used for a given installation.
As you move to step 2 for ambient you can now easily choose the correct column to use based on the header. Temperature
Rating of the conductor.
If your using 90 c for step one use 90c for step two.
If the example THWN/ THHN is use in a wet location you use 75c in step one and in Step 2. If this conductor is used in a dry location you can use 90c for step one and 90c for step two.
Now that this is done go to step three number of conductors.
Now you have the final conductor ampacity.
Step 1: Conductor ampacity based on insulation type.
Step 2: Correction of ambient
Step 3: Adjustment of # of
conductors.
Final ampacity for conductor based on it's insulation type use correct column from table.
Hope this helps.